Extension cord gauge question



 
 
Thread Tools Display Modes
  #1  
Old June 20th 09, 03:06 PM posted to rec.aviation.soaring
Tuno
external usenet poster
 
Posts: 640
Default Extension cord gauge question

Yes, I know I'm a little OT here, but I am packing for Parowan

I recall someone once telling me that extension cords larger than 14
gauge (maybe he said 16) are a waste of money because the plugs at
each end are not rated for anything higher than what a 16 gauge wire
can provide.

Is this true in general?

I want to pack a 50 foot extension cord to use with the motorhome (on
a 20 amp circuit) and I want to get something "gauge appropriate".

-ted/2NO
  #2  
Old June 20th 09, 05:14 PM posted to rec.aviation.soaring
QT[_2_]
external usenet poster
 
Posts: 16
Default Extension cord gauge question

On Jun 20, 10:06*am, Tuno wrote:
Yes, I know I'm a little OT here, but I am packing for Parowan

I recall someone once telling me that extension cords larger than 14
gauge (maybe he said 16) are a waste of money because the plugs at
each end are not rated for anything higher than what a 16 gauge wire
can provide.

Is this true in general?

I want to pack a 50 foot extension cord to use with the motorhome (on
a 20 amp circuit) and I want to get something "gauge appropriate".

-ted/2NO


I carry 2 50' 30A cords with a 3015 adapter. Bulky but low loss.
Appropriate gauge is a function of length as will as amps.
  #3  
Old June 20th 09, 05:37 PM posted to rec.aviation.soaring
Darryl Ramm
external usenet poster
 
Posts: 2,403
Default Extension cord gauge question

On Jun 20, 7:06*am, Tuno wrote:
Yes, I know I'm a little OT here, but I am packing for Parowan

I recall someone once telling me that extension cords larger than 14
gauge (maybe he said 16) are a waste of money because the plugs at
each end are not rated for anything higher than what a 16 gauge wire
can provide.

Is this true in general?

I want to pack a 50 foot extension cord to use with the motorhome (on
a 20 amp circuit) and I want to get something "gauge appropriate".

-ted/2NO


Ted

What the person probably meant is the standard electrical plugs and
sockets are rated by current, it is not really whether the pins or
junction between the pins and wire will carry the current (although in
the long run that is a part of the NEMA design) but what wiring and
breaker is behind that socket in the wall. An outlet intended to
supply 20 Amps whould have a NMEA 5-20R outlet wth a T-shaped neutral.
Ideally you would look for an extension cord that also had 5-20
connectors at each end. If you find a cord with 5-20 connectors and
its 50' long it will be rated for 20 amps. But a nice heavy cord with
5-15 connectors will plug into a 5-20 socket.

See what other marking to look for here
http://www.osha.gov/SLTC/etools/cons...iblecords.html

See the range of NMEA connectors at http://www.twacomm.com/catalog/dept_id_963.htm
and http://en.wikipedia.org/wiki/NEMA_connector


Darryl
  #4  
Old June 20th 09, 06:50 PM posted to rec.aviation.soaring
vaughn
external usenet poster
 
Posts: 93
Default Extension cord gauge question


"Tuno" wrote in message
...
I want to pack a 50 foot extension cord to use with the motorhome (on
a 20 amp circuit) and I want to get something "gauge appropriate".


In general, you need at least a #12 conductor to safely conduct 20 amps
(#14 for 15 amps). For a 50 foot 20-amp cable, I would prefer #10 for less
voltage drop (highest efficiency).

Vaughn


  #5  
Old June 21st 09, 03:56 AM posted to rec.aviation.soaring
Steve Koerner
external usenet poster
 
Posts: 430
Default Extension cord gauge question

a 50 ft cable introduces 100 feet of wire for voltage drop
calculation. For 20 amp load, here's the voltage drops:

10 ga -- 2.4 volts
12 ga -- 3.7 volts
14 ga -- 5.9 volts

I wouldn't have much hesitation about using a 14 gauge cable if that's
what I had but if I were going out to buy one I'd look for 12 gauge as
10 gauge is expensive and bulky and only makes a 1% difference.
 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Puchacz shock cord (bungee) failure [email protected] Soaring 4 July 1st 06 09:18 PM
Spectra cord for ground launch ttaylor at cc.usu.edu Soaring 1 September 10th 05 05:13 AM
Can anyone help, PLEASE - searching for zip-cord (aka: mono-cord, speaker wire, shooting wire, dbl hookup, rainbow cable, ribbon cable) Striker Cat Home Built 6 October 15th 04 08:51 PM
Can anyone help, PLEASE - searching for zip-cord (aka: mono-cord, speaker wire, shooting wire, dbl hookup, rainbow cable, ribbon cable) Striker Cat General Aviation 0 October 12th 04 05:11 PM